D dinkelja Member Oct 11, 2007 #1 Poll: What ampacity adjustment factor might you use on four multicondutor cables, each with four current carrying conductors?
D dinkelja Member Oct 11, 2007 #3 rr, I take that as you mean 50%. How about if I de-rated the conductors within the cables frist, then the group of 4 cables = 64% Any takers?
charlie b Moderator Staff member Location Lockport, IL Occupation Retired Electrical Engineer Oct 11, 2007 #4 The rule has to do with the number of conductors, not the way the conductors are grouped.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Oct 11, 2007 #5 charlie b said: The rule has to do with the number of conductors, not the way the conductors are grouped. Click to expand... I agree,16 CCC's would require a derated value of 50%.