When you have neutrals from different circuits but the same system contained in the same junction box, is it permissible to tie them all together?
Thanks,
matt
Thanks,
matt
That not only creates parallel paths for the neutral, as Bob points out, but if this is resi work, it will cause problems with the functionality of your AFCI's. There is definitely a certain "style" of installer who connects all the whites together, but this has always been wrong. It also creates a hazard for the person servicing the installation in the future.Minnesotaelectric said:When you have neutrals from different circuits but the same system contained in the same junction box, is it permissible to tie them all together?
iwire said:In my opinion no, that would be a violation of 310.4
Dennis Alwon said:This will definitely cause unwanted emf's
frizbeedog said:310.4
1/0 and larger.
Bob?
That would be one big wire nut. Probably have to put in on with an impact wrench.iwire said:Do you think he was talking about wire nutting multiple neutrals together that are 1/0 and larger?
I kind of assumed he was talking 12s and 14s.![]()
iwire said:Do you think he was talking about wire nutting multiple neutrals together that are 1/0 and larger?
frizbeedog said:No I didn't.
Just wondering why that article was refrenced
frizbeedog said:No I didn't.
Just wondering why that article was refrenced
mdshunk said:but if this is resi work, it will cause problems with the functionality of your AFCI's.
iwire said:'Cause it's the right code section?![]()
That section, outside of it's exceptions does not permit the paralleling of conductors smaller then 1/0. If you have multiple circuits in a box and tie all the neutrals together then you have put at least some of them in parallel.
Dennis Alwon said:Yep.....
![]()
frizbeedog said:How much do I owe you?
stickboy1375 said:If you really want to scare yourself, go out and buy a gauss meter and try getting away from high levels of EMF's...![]()
iwire said:Life is dangerous, live healthy, die anyway. :wink:
stickboy1375 said:Living past your prime is pretty much senseless anyway.... :grin:
iwire said:Well it's been nice knowing you all, I am off to suck on a tail pipe.![]()