don_resqcapt19 said:Jon,
I fully agree, but the CMP 6 does not. I submitted a proposal for the 2008 code to change this, but the CMP insists that the words "shall be permitted" actually prohibit any other installation...I wonder where they studied the English language?
OK im gonna get off topic for a second!!
AH HA!! LOL Just as i suspected!! Remember that 'little' debate er uh i mean 'discussion'
go here to post #46
http://forums.mikeholt.com/showthread.php?t=100861&page=5
I said basically the same thing what they are saying in there little response you typed. when they put up the exceptions it looks like they were intending to have a restriction in the comment 'shall be permitted' even though it does not say 'shall not be allowed'. Thats the logic they are using there.
brother said:there is a DIRECT statement in 250.104(A)(1) that says "metal water piping system installed in or attached to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductore where of sufficient size, or to the one or more grounding electrodes used.
CMP 6 said:The language specifically
allows conductors 1/0 or larger to be run in parallel, which means conductors
smaller than 1/0 in general are not permitted to be run in parallel.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
Also another of my comments from that line of reasoning
brother said:I was not stating that those additional sections 2, 3 limited the extra bonding, I was stating that if they (CMP) DID not intend to limit it in the 1st section then there would be NO need for the EXCEPTIONS. Thats just basic reasoning and reading it in context. Thats how they do all the code sections, if they did not intend to limit something then there would be no need for an exception, would you not agree ??
Ok, im not wanting to debate that topic again, 'Bonding subpanel' just wanted to point something out.