Multiple power source conductors in same raceway

Status
Not open for further replies.

csoc64

Senior Member
Location
northeast
Is there anything in the code that says that I cannot run conductors from different power sources in the same raceway? On a recent installation, I ran a set of conductors for a dedicated receptacle (for Envoy monitor) through the same conduit containing the production meter load side conductors that ran to the pv breaker in the main panel. I was questioned by the inspector on this, but he could not reference a code article and did to not fail me for it.
 
Running AC inverter outputs with other AC circuits is fine.

You're not allowed to run DC photovoltaic conductors in the same raceway as other types of systems, unless you have a partition. That's 690.4(B). But that doesn't seem to apply here.
 
Running AC inverter outputs with other AC circuits is fine.

You're not allowed to run DC photovoltaic conductors in the same raceway as other types of systems, unless you have a partition. That's 690.4(B). But that doesn't seem to apply here.
Unlike the output of a generator, the output of a grid-tied inverter is part of the same combined system, not a separate system.
 