Here is the set up, every thing 120/240 single phase. Utility power into a ATS from service disconnect. ATS then supplies a MDP that runs lights, A/C and gen use recpts. also out of MDP it feeds a service switch with a UPS that powers a UPS panel that runs communication equipment.
Some one connected a piece of equipment in the UPS panel that should not have been. It should have been feed from the MDP. The guys that were sent to correct this wanted to just install another piece of conduit from the UPS panel to the MDP, make a splice in the panel and carry it to the MDP. I said that I did not think that was code due to the fact that the UPS panel had a separate power source aside from the normal utility or gen. power that the panel would receve from the MDP. Am I wrong on this?
Some one connected a piece of equipment in the UPS panel that should not have been. It should have been feed from the MDP. The guys that were sent to correct this wanted to just install another piece of conduit from the UPS panel to the MDP, make a splice in the panel and carry it to the MDP. I said that I did not think that was code due to the fact that the UPS panel had a separate power source aside from the normal utility or gen. power that the panel would receve from the MDP. Am I wrong on this?