I think it is time to post the relevant NEC code sections, as always local or other codes may have an impact as well.
The above section has to do with interior receptacle outlets and has nothing to do with exterior signs.
Now this section requires a sign outlet at each entrance but it does not require that it be used.
210.62 Show Windows. At least one receptacle outlet
shall be installed within 450 mm (18 in.) of the top of a
show window for each 3.7 linear m (12 linear ft) or major
fraction thereof of show window area measured horizontally
at its maximum width.
The above section has to do with interior receptacle outlets and has nothing to do with exterior signs.
600.5 Branch Circuits.
(A) Required Branch Circuit. Each commercial building
and each commercial occupancy accessible to pedestrians
shall be provided with at least one outlet in an accessible
location at each entrance to each tenant space for sign or
outline lighting system use. The outlet(s) shall be supplied
by a branch circuit rated at least 20 amperes that supplies
no other load. Service hallways or corridors shall not be
considered accessible to pedestrians.
Now this section requires a sign outlet at each entrance but it does not require that it be used.