wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
I don't agree. The electrode is the "metal underground water pipe" meeting certain conditions. If the intention were "water pipe of which at least 10 ft is underground" that would have been the wording.Note the language in 250.52(A)(1) "electrically continuous ... to the points of connection of the GEC", and how the sentence structure implies that's all part of the electrode.
Also, there are other cases of extending an electrode for a connection. E.g. stubbing up rebar out of a concrete-encased-electrode to connect the GEC to.
The logic seems pretty clear to me: whatever the extent of the electrode is, we could connect our GEC to anywhere along that extent. So portions of the water pipe to which we are prohibited from connecting our GEC, like more than 5 ft to the interior of the building (barring the exception), must not be part of the electrode.Now consider whether anything in the 5ft rule language directly contradicts this implication.
Cheers, Wayne