How many people bond to every metal water pipe leaving the building?
I have a water treatment plant project with an influent and an effluent leaving the building. It was my interpretation as required per code according to 250.50 that I have to bond the metal underground water pipe. It was not my interpretation that I would have to bond every metal underground water pipe that is in direct contact with the earth, and so I bonded to the influent piping within five feet of where it enters the building and did not bond the effluent knowing that it has is effectivly bonded via piping. The inspector is requiring us to bond both the influent and the effluent, and said that if we had 100 pipes we would have 100 bonding points regardless of whether or not the piping was effectlivly bonded via piping. What are your thoughts?
I have a water treatment plant project with an influent and an effluent leaving the building. It was my interpretation as required per code according to 250.50 that I have to bond the metal underground water pipe. It was not my interpretation that I would have to bond every metal underground water pipe that is in direct contact with the earth, and so I bonded to the influent piping within five feet of where it enters the building and did not bond the effluent knowing that it has is effectivly bonded via piping. The inspector is requiring us to bond both the influent and the effluent, and said that if we had 100 pipes we would have 100 bonding points regardless of whether or not the piping was effectlivly bonded via piping. What are your thoughts?