kbruin
Member
- Location
- Denver, CO, USA
I am designing a multi circuit light panel and circuits for a room and would like to check I am interpreting NEC appropriately for the application.
Scenario:
-9x 115v circuits (single pole 20A breakers)
-Each circuit feeds a single duplex receptacle
-Receptacles are fed from a UL 508A industrial control panel
-Panel feed is 120v/208v, 3 phase, 4 wire wye
-A single 3/4" liquid tight non metallic conduit runs from the panel and feeds the 9 receptacles
-Use #12 THHN wire for all conductors (hot, neutral, ground)
-3 sets of 4 wires (phase 1, phase 2, phase 3, neutral) will be used
-Each receptacle will have 2x 660w LED fixture plugged in.
NEC Considerations:
-Per 310.15(B)(5)(a) I am not counting the neutrals in each set of 4 wires giving 9 current carrying conductors
-Per 310.15(B)(3)(a) I am derating the #12 THHN by 70% and from table 310.15(B)(16) the 30 Amp rating becomes 21 Amps (protected by 20 Amp single pole breakers)
-Per Annex table C.5 I am allowed 16 conductors in 3/4" in liquidtight flexible nonmetallic conduit (there are 12 in this scenario)
Questions:
A) Am I applying the neutral exception appropriately?
B) For these multiwire circuits do I need to use either a 3 (or even 4) pole breaker or single poles with handle ties?
C) As the lights are unpluggable, would we run into an adverse or unsafe situation where, assuming the circuits are energized, the first set of 2 lights are plugged in and turned on while the other 2 sets of 2 lights are unplugged (due to the shared neutral)?
Alternative:
I can avoid having to do any 'funny business' if I were to run 18 wires (hot and neutral for each circuit), rate as if they are all current carrying (derate 50%), use #10 wire, and 1-1/4" conduit. As you can see the alternative is going to be significantly more expensive. Any and all thoughts on how to tackle the design requirements here would be appreciated. Let me know if more information regarding the scenario is needed to give an exact answer.
Scenario:
-9x 115v circuits (single pole 20A breakers)
-Each circuit feeds a single duplex receptacle
-Receptacles are fed from a UL 508A industrial control panel
-Panel feed is 120v/208v, 3 phase, 4 wire wye
-A single 3/4" liquid tight non metallic conduit runs from the panel and feeds the 9 receptacles
-Use #12 THHN wire for all conductors (hot, neutral, ground)
-3 sets of 4 wires (phase 1, phase 2, phase 3, neutral) will be used
-Each receptacle will have 2x 660w LED fixture plugged in.
NEC Considerations:
-Per 310.15(B)(5)(a) I am not counting the neutrals in each set of 4 wires giving 9 current carrying conductors
-Per 310.15(B)(3)(a) I am derating the #12 THHN by 70% and from table 310.15(B)(16) the 30 Amp rating becomes 21 Amps (protected by 20 Amp single pole breakers)
-Per Annex table C.5 I am allowed 16 conductors in 3/4" in liquidtight flexible nonmetallic conduit (there are 12 in this scenario)
Questions:
A) Am I applying the neutral exception appropriately?
B) For these multiwire circuits do I need to use either a 3 (or even 4) pole breaker or single poles with handle ties?
C) As the lights are unpluggable, would we run into an adverse or unsafe situation where, assuming the circuits are energized, the first set of 2 lights are plugged in and turned on while the other 2 sets of 2 lights are unplugged (due to the shared neutral)?
Alternative:
I can avoid having to do any 'funny business' if I were to run 18 wires (hot and neutral for each circuit), rate as if they are all current carrying (derate 50%), use #10 wire, and 1-1/4" conduit. As you can see the alternative is going to be significantly more expensive. Any and all thoughts on how to tackle the design requirements here would be appreciated. Let me know if more information regarding the scenario is needed to give an exact answer.