In addition to the obvious reduction in number of CCCs counted for derating, there is a quite significant reduction in voltage drop on a balanced circuit.
With two circuits and two neutrals, the VD on. 120V circuit is twice the drop in the hot conductor.
With an MWBC the voltage drop on each circuit is just that of its own hot wire.
An earlier post stated that the MWBC is more efficient, and this difference in voltage drop is where that comes from.
Cost is also lower for less copper.