I have a question about 210.4 (2002).
If I have a 480V 3 phase system and 480V lighting fixtures is the following setup considered a multiwire branch circuit and code compliant?
I have a 3 pole breaker that feeds (3) 480V lighting circuits. The circuits are fed evenly across the three phases (with line to line circuits across two phases) to get the 480V. So the circuit has a conductor from each of the three poles of the 3 pole breaker and a single EGC. There is no neutral.
I guess I'm confused about 210.4(C) which requires multiwire branch circuits to only supply line to neutral loads. However, exception no. 2 seems to allow the line to line connections that I have.
If I have a 480V 3 phase system and 480V lighting fixtures is the following setup considered a multiwire branch circuit and code compliant?
I have a 3 pole breaker that feeds (3) 480V lighting circuits. The circuits are fed evenly across the three phases (with line to line circuits across two phases) to get the 480V. So the circuit has a conductor from each of the three poles of the 3 pole breaker and a single EGC. There is no neutral.
I guess I'm confused about 210.4(C) which requires multiwire branch circuits to only supply line to neutral loads. However, exception no. 2 seems to allow the line to line connections that I have.
Last edited: