The webmaster disabled hyperlinks as a temporary measure for combatting SPAM. He has put into place a process that, so far, seems to be sucessful in preventing the advertisements and worse topics that have been posted over that past month or two. He is working on getting the hyperlinks re-enabled. It should not be long before you can use them again.Smart $ said:So where is it that hosts linkable images for free... since we no longer can attach them???
Smart $ said:I get, using my vector diagram technique:
- A = 18.0A @ 0?
- B = 14.6A @ -128.2?
- C = 14.6A @ -231.8?
A B C
2.5 2.5 2.5
2.5 1.5 1.5 =
5kva 4kva 4kva
/ 277 / 277 / 277 =
18A 14A 14A
Well, not quite. Panel schedules [generally] do not have two entries per pole (re: your 2.5's and 1.5's), and approximated kva values are just that... approximated.ramsy said:Am I looking at a panel schedule?, if so I like it.
Thanx, Julie.tallgirl said:
Smart $ said:A quick way to get a more accurate value for unbalanced line-to-line loads is with this formula..
* sqrt(a^2 + b^2 + a*b)
charlie b said:It is not technically correct to speak of “current across two phases.” ..This is a three phase system,
charlie b said:The webmaster disabled hyperlinks as a temporary measure for combatting SPAM. He has put into place a process that, so far, seems to be sucessful in preventing the advertisements and worse topics that have been posted over that past month or two. He is working on getting the hyperlinks re-enabled. It should not be long before you can use them again.
Afraid not.ramsy said:That looks familiar, and much simpler than vector graphs. I checked the NEC to see if I could use it without Engineering supervision.
That particular example simply divided the lighting load, which individually are line to neutral loads, among the two phases.I didn't find any NEC references, but there is a NFPA 70 substitute in Appendix D, Ex. No. D5(a & b), which was calculated from 2 legs of a 3? 208Y, as VA / #legs / V? [/ PF] = I?
That's because the method of calculation assumes the loads to be balanced (1:1) and uses a 1.732 adjustment factor, or 0.866 per load. Being unbalanced at 5:3, the adjustment factor calculates to be 0.875 per load.My previous attempt to match your vector results with a panel schedule was a similar method, but without rounding down the B & C phase are 14.44A vs 14.58A for the vector.
The portion of Example 5 you referred to has nothing to do with unbalanced loads. However, it does have a portion dealing with potential unbalanced loads in the service to meter bank feeder section. The procedure compensates by doubling the number of ranges, applying the appropriate demand factor, halving the demand per phase, then multiplying by three to arrive at a system VA. IMO, the NEC is saying the error is not negligible by doubling the number of ranges. The rest of the procedure is SOP.Whether the NEC-engineering panels' use of Ex. D5 suggests this approximation error is negligible or not --relative to vectors-- if permitted to represent unbalanced loads this way, I find that both 3? and 1? panel schedules are much simpler to build with simple division.
The phase mutual to the loads. For example, if a represents load AB and b represents load AC, the result correlates to A-phase.Using all 3 phases, I could not make sense of which 2 load variables using sqrt(a^2 + b^2 + a*b) matched which of the 3 phases.
Yes, the circuit should have conductors and OCPD sized to the phase with the highest draw. This was my point for entering this discussion to begin with. As for the "panel schedule method", with branch circuits and feeders uprated 125% I believe you can do that safely :smile:Perhaps with a 3-pole OCPD sized for the highest one it doesn't matter, but life seems easier for all L-L, L-N, un/balanced loads if conductor sizing is permitted with that panel-schedule method I did, originally derived from KingPd.
If I recall correctly, there wasn't any way to attach a java program.tallgirl said:I was going to write and attach a Java program to draw vector diagrams like what Smart used to post, but now that we can't do attachments ...
Smart $ said:..if a represents load AB and b represents load AC, the result correlates to A-phase. ..the circuit should have conductors and OCPD sized to the phase with the highest draw. This was my point for entering this discussion