Estoy de acuerdo.
Then what are 100 and 101? :wink:
Don't forget in the 2008 NEC 210.4 (B) every multiwire branch circuit must now have either a multipole breaker or handle tie to disconnect all ungrounded conductors simultaneously. The option to this of course is to provide a neutral conductor for each hot. At this point, every wire is considered a CCC so watch 310.15(B)(2)(a).
Also in the 2008 code is that all conductors that share a neutral leaving a panel where there are multiple conductors in conduit, must be wire tied together.
Not necessary, because you'll be using only the two 120v-to-N lines, and the single-phase neutral isn't succeptable to harmonic issues.How about if you have a 120/240v 3 phase delta transformer and you are taking two hots and a neutral to linear or nonlinear loads do you count the neutral as a current carrying conductor?
No again, because you'll use either the three phases without the neutral for 3-phase loads, or the two 120v-to-N lines for 1-ph loads, but never both to the same load.How about three hots and a neutral?
The neutral is only in use for 1-ph loads, so correct.Would it carry just the imbalaced load per 310.15(4)(a) and not be required to be counted?
ON a 208 v 4 wire if i use two hots and a neutral how many CCC do i have? ON A 240 V SINGLE phase two hots one neutral how many CCC? (no harmonics)
Multiwire branch circuits...that eliminates the 208v loads. Still, if the loads are balanced, maybe 2 identical lighting circuits, would the neutral be current carrying?
The first one is correct, the second is not (if we're talking about a 3ph source.)Wouldn't it depend on the load? If it is a 208v load then the neutral would serve no purpose and not be current carrying. If it is 2 120v loads and they are balanced, then the neutral would still not carry any current. Or am I missing something?
Again, think of a balanced-loaded 3 x 120v system. The neutral carries no current. Now, for each amp you reduce one phase's current by, the neutral current increases by the exact same amount.Oops...I guess i should have read the title...Multiwire branch circuits...that eliminates the 208v loads. Still, if the loads are balanced, maybe 2 identical lighting circuits, would the neutral be current carrying?
It should be exactly the same, if my theory above pans out.Two identical loads supplied from MWBC on a 208Y/120 volt system would have a neutral current of about the same current as the phase current.
I think I might be getting it. Since it is a 3 phase system the sine waves are not exactly opposite, as they would be on the neutral in a single transformer system, therefore the currents do not exactly oppose each other so there is actually current flow on the neutral.
Something like that?
Very much like that. With single-phase, the opposing lines ("phases") reach their peaks at the same moment, so any current traveling equally through both lines send no current through the neutral.Something like that?