Just a quick question, any input is welcome and very much appreciated. When and how is it legal according to the 2017 NEC to use 12/3 NM-B cable for multiple receptacle or lighting circuits in a residential setting?
Thanks.
But can you not use 12/3 on tied single pole breakers?Perfectly legit. However you would not want to. Ask yourself how are you going to AFCI the circuits? 2 pole AFCI are expensive. Some manufactures allow single pole to be used and they will need to be handle Tied.
I would not it just complicates things.
But can you not use 12/3 on tied single pole breakers?
Sent from my SM-N910V using Tapatalk
Anytime you wish to do so, as long as you meet some requirements.
210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall
be permitted as multiwire circuits. A multiwire circuit shall be
permitted to be considered as multiple circuits. All conductors
of a multiwire branch circuit shall originate from the same
panelboard or similar distribution equipment.
Informational Note No. 1: A 3-phase, 4-wire, wye-connected
power system used to supply power to nonlinear loads may
necessitate that the power system design allow for the possibility
of high harmonic currents on the neutral conductor.
Informational Note No. 2: See 300.13(B) for continuity of
grounded conductors on multiwire circuits.
(B) Disconnecting Means. Each multiwire branch circuit shall
be provided with a means that will simultaneously disconnect
all ungrounded conductors at the point where the branch
circuit originates.
Not allowed for stand-alone power systems (Off Grid Solar Arrays, Batteries, or Generators), 710.15(C)
See all restrictions by searching the 2017 NPFA-70 PDF for keyword "multiwire"
Yes you can use 12/3 or 14/3 as long as the breakers have a handle tie and of course are not on the same phase. I did not state the obvious as we are all supposed to know that you cannot have both circuits on the same phase.
Thanks
I don't see where stand alone power system is relevant to this topic?
Thx. I'm new here, and learning.Yes you can use 12/3 or 14/3 as long as the breakers have a handle tie and of course are not on the same phase. I did not state the obvious as we are all supposed to know that you cannot have both circuits on the same phase.
Thanks
I don't see where stand alone power system is relevant to this topic?
Just a quick question, any input is welcome and very much appreciated. When and how is it legal according to the 2017 NEC to use 12/3 NM-B cable for multiple receptacle or lighting circuits in a residential setting?
Thanks.
Just a quick question, any input is welcome and very much appreciated. When and how is it legal according to the 2017 NEC to use 12/3 NM-B cable for multiple receptacle or lighting circuits in a residential setting?
Thanks.
You might also want to consider using either 12/2/2 or 14/2/2 NM for this type of installation. You have two separate circuits but only one cable/homerun.
You save one ground wire!
That is another benefit. I use these cables quite a bit on remodels and room additions.
Maybe the residence in question is off-grid? :angel:
Residences in Florida and several US territories went off grid, after recent hurricanes.
710.15(C) prohibits MWBC's for "Stand-Alone Systems" preferred in off-grid areas.
WARNING:
SINGLE 120-VOLT SUPPLY. DO NOT CONNECT MULTI‐
WIRE BRANCH CIRCUITS!
The warning sign(s) or label(s) shall comply with 110.21(B).
I don't think the OP being in New York is concerned about off grid applications. I could be mistaken.
Whats A-Matter You, Why You Looka So Sad, It's A-Not So Bad, just because this topic is relevant to Residential "Stand-Alone Systems" that are installed everywhere, not just Off-Grid areas.