This seems to be unanimous. Let us know if you were able to get the inspector to change his mind.
I spoke with the inspector this morning. I wasn't able to convince him at first, but he spoke with his senior inspector who confirmed that it wasn't a violation. The junior inspector called me back and there is no problem now.
Next time I see him I will tell him about this forum.
I spoke with the inspector this morning. I wasn't able to convince him at first, but he spoke with his senior inspector who confirmed that it wasn't a violation. The junior inspector called me back and there is no problem now.
He did mention he thought the receptacle might need to be tamper proof according to 2008 code, but said the NEC isn't exactly clear about plugs in a cabinet underneath the kitchen sink, so he passed me.
Well he was right about the tamper resistant requirement when you're under the 2008 NEC.
I'm not sure I understand your response.
Are you saying the inspector was correct when he said a tamper resistant recep is not required in the 2008 code? [I don't see that the 2011 has changed this].
IMO, although I think this is not the intent, 210.52 does not include receptacles under the sink. Thus if a receptacle is installed for a disposal and dw under the sink, then it would not need TR.
Yes, the way the 2008 was written the requirement was somewhat ambiguous. The 2011 cleared this up.
Exception (3) in 2011 seems to allow non TR for Appliance area dedicated spaces. I guess the disposal area under the sink is not a dedicated space.In all areas of 210.52 all non locking type 125v 15 and 20 amp receptacles shall be listed TR.
Substantiation: By allowing the exception for a single receptacle or duplex receptacle located within dedicated space will eliminate the need for tamper-resistant receptacles to be installed behind dishwashers, refrigerators, washing machines and the like.
Panel Statement: CMP-18 accepts in principle the intent of ?behind
appliances? see panel action and statement on Proposal 18-71.
Derek I do tend to agree with you and I believe that is the intent. I wish they would just say all areas of a dwelling and attached buildings and leave it at that. I can't imagine too many ec's taking advantage of this except perhaps someone doing large apts. It may be worth it but I bet you spend more time with employees trying to keep things straight and having the correct recep. available.I am not so sure that the receptacle under a sink for a disposal and/or dishwasher does not need to TR.
The receptacle under the sink is not behind the appliance it serves blocking access from a child nor is the area dedicated to an appliance only.
Derek I do tend to agree with you and I believe that is the intent. I wish they would just say all areas of a dwelling and attached buildings and leave it at that. I can't imagine too many ec's taking advantage of this except perhaps someone doing large apts. It may be worth it but I bet you spend more time with employees trying to keep things straight and having the correct recep. available.
I am not so sure that the receptacle under a sink for a disposal and/or dishwasher does not need to TR.
Here is the substantiation for the proposal, 18-71, that was submitted for the exception that the CMP accepted:
The receptacle under the sink is not behind the appliance it serves blocking access from a child nor is the area dedicated to an appliance only.
I pulled this from ROP 18-81:
ROP substantiations often have items that do not end up in the code.
2008 & 2011 [406.11 or 406.12] say, "...all areas specified in 210.52.' I cannot find anything in 210.52 that addresses undersink receps for dishwasher/disposals.
As an inspector I just refuse to tag someone if I can't back it up with a code section [or UL listing, etc.].
Yeah, it probably creates more confusion than it is worth. What is the price difference between a standard and a TR rec? I am curious.