250.32(a) Exception allows a single branch circuit w/gnd to supply a separate building without that building needing a grounding electrode. Does a multiwire branch circuit w/gnd qualify under this exception?
 
Re: Multiwire question

Branch Circuit , Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.

225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure served that is on the load side of the service disconnecting means shall be supplied by one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.

Looks like it to me
 