brother
Senior Member
I'm curious how other areas handle this. I told a guy that since he added another 4 receptacles to an existing circuit (basically altering it) that he had to comply with 2008 NEC 210.4(B). Basically 3 circuits sharing a neutral, but in the panel they do not presently have a common disconnect (3 pole breaker or 3 single pole with handle tie). Even though I do not agree with this 2008 NEC code change on this, I still comply with it.
He claims it is an existing circuit and that he did not install a new circuit and that just adding a 2 duplexes to it is not enough to cause a compliance with the NEC 2008.
Basically his resistance is mainly because they do not make 3 pole handle ties for these 3 single pole breakers because they are so old. The reason he didn't want to do a breaker swap out is because of all the stuff he has to go through to get a panel shutdown to do this. This job is in a hospital.
What is your opinion and how does your Inspectors enforce it??
He claims it is an existing circuit and that he did not install a new circuit and that just adding a 2 duplexes to it is not enough to cause a compliance with the NEC 2008.
Basically his resistance is mainly because they do not make 3 pole handle ties for these 3 single pole breakers because they are so old. The reason he didn't want to do a breaker swap out is because of all the stuff he has to go through to get a panel shutdown to do this. This job is in a hospital.
What is your opinion and how does your Inspectors enforce it??