I have been useing GFCI outlets in the attic for the eqipment . My helper says a regular outlet is okay. What do y'all do?
Thanks
Buck
Thanks
Buck
buckofdurham said:I have been useing GFCI outlets in the attic for the eqipment . My helper says a regular outlet is okay. What do y'all do?
Thanks
Buck
480sparky said:Unless whatever you are plugging in requires a GFI by it's instructions.
celtic said:Aren't they requiring "whatever you are plugging in requires a GFI" to come with it's on intergral GFI protection? (Blow dryers, vending machines, etc)
480sparky said:Who is 'they'? It's not an NEC thing, I'm thinking NEMA??
don_resqcapt19 said:The user must comply with the second part of 590.6(B).
Don
590.1 Scope The provisions of this article apply to temporary electric power and lighting installations.
That is correct, the attic outlet is not a trmporary installation, however the cord that is plugged into it is and 509.6(A) requires the user to provide the GFCI protection if the "temporary" power is used for maintenance purposes.IMO the receptacle in the attic would not qualify as a temporary installation. It is installed permanently so a maintenance person can easy plug in power tools and other equipment.
Yes, per the code rule, however that part of the rule does not really belong in the code.Even when the user is the HO?
590.6 Ground-Fault Protection for Personnel
Ground-fault protection for personnel for all temporary wiring installations shall be provided to comply with 590.6(A) and 590.6(B). This section shall apply only to temporary wiring installations used to supply temporary power to equipment used by personnel during construction, remodeling, maintenance, repair, or demolition of buildings, structures, equipment, or similar activities.
(A) Receptacle Outlets All 125-volt, single-phase, 15-, 20-, and 30-ampere receptacle outlets that are not a part of the permanent wiring of the building or structure and that are in use by personnel shall have ground-fault circuit interrupter protection for personnel. If a receptacle(s) is installed or exists as part of the permanent wiring of the building or structure and is used for temporary electric power, ground-fault circuit-interrupter protection for personnel shall be provided. For the purposes of this section, cord sets or devices incorporating listed ground-fault circuit interrupter protection for personnel identified for portable use shall be permitted.
M. D. said:So Don , when I use a vacuum in the every day maintenance of my house , unless it is gfci protected when I plug it in ,...I have violated 590.??