- Semi-Retired Electrical Engineer
This is not a problem. Current will always find its way back to its source. If the generator is on line, it is the source. Current leaving the generator and heading to the 3 phase loads will return either by the phase conductors (if all is balanced) or by the neutral (if there is some imbalance). Once it returns to the N-G bond point on the generator system, the fact that the utility?s neutral is essentially connected to that same point is not relevant. Current will not flow backwards along the utility?s neutral and into the utility?s distribution system, because there is no driving force to push it in that direction. The same is true for current leaving the generator and heading towards the single phase loads.