OHSA mandate for protection of utility line man against arc flash is mentioned in this article.
https://googleweblight.com/I?u=http...tility-linemen-from-arc-flash-events&hl=en-IN
I am tempted to say "You can touch my wires anytime you want to", but I think I won't.
AFAIK nobody is required to follow 70E, but doing so is the easiest way to comply with what OSHA does require. One can create their own safety standard but it will take a lot of time and effort to establish it and keep it up to date with new technology or findings, simply using 70E lets someone else do all that work of keeping things up to today's needs. There may possibly be other publications that do about the same thing out there but 70E is most popular.PPE is not intended to prevent injury. It is intended to keep you from non-recoverable injury. It is rated in Cal/cm^2. Not voltage or current.
Utilities per se do not have to follow NEC 70E, but OSHA would definitely stick their nose in. I wouldn't want to be the guy on the stand being asked the question:
"So, one of your workers was killed, correct"
Yes.
"Was he wearing proper PPE"
Well, I don't know. We hadn't done an arc flash assessment.
"Why is that?"
We are a utility, and arn't governed by the NEC
"So, you had them work on hot lines, without proper safe guards?"
Well, we told them to be careful.
Your honor we request our clients family be awarded $300 Million Dollars; Granted.