HOW CAN SIZING OF THE MV SWITCHGEAR BUSBAR ACCORDING TO NEC ?, IS THERE IS ANY RELATED ARTICLE IN NEC
PLEASE ADVISE
PLEASE ADVISE
Bus bar size inside switchgear is determined by building a structure & subjecting it to a heat run test. The bars are loaded to the the rated ampacity & then the temperature is measured over a period of hours or until it is stabilized. The temperature is only allowed to rise by so many degrees above the ambient.
In some cases like 4000A mains, blowers will force cool the 3000A rated bus & breaker.
In the gear that I have sold over the past 20 or so years I have never seen a requirement for fans to cool bus in any specs of otherwise.
Selecting a bus size is based upon temperature rise.
ntalling bus is based upon the require L-L, L-N, And L-G clearances as well is the insulators and support requirements for fault current bacing requirements.
Selecting a bus size is based upon temperature rise. ntalling bus is based upon the require L-L, L-N, And L-G clearances as well is the insulators and support requirements for fault current bacing requirements.
MV swgr assemblies a manufactured to applicable NEMA/ANSI/and IEEE standards.
For MV metal clad gear covered by IEEE C37.20.2 standard ratings are defined as 1200A, 2000A, and 3000A. Some manufacturers offer 4000A gear that meets the temperature rise requirements by using fans. Most sophisticated customers will not buy this fan cooled switchgear. A similar phenomenon exists for LV switchgear - typical ratings go up to 4000A, but 5000A gear is avaiallble if the user is willing to accept a number of compromises like forced air cooling, uninsulated bus, etc.
This is correct, but the key is that the temperature rise of the bus is affected by the enclosure and barrier design, that's why the IEEE switchgear standards require a heat run for the whole assembly to take into effect the enclosure without any guessing, rules of thumb, or calculations.
This is essentially correct in that there are rules of thumb for these clearances, but the only requirement in the IEEE standards is that the equipment passes all of the tests, including the BIL test - actual clearances are not specified.
I'm just going by the Westinghouse gear that I sold, both MV and LV the old DHP one of the original VCP, then the VCPW, DS, Magnum DS, etc. I have taken my customers on factory tours and have never seen fans used to cool bus in either indoor/outdoor, or walk in electrocenters. Yesthe original design must be tested to assure that it complies with temperature rise. These test may be an option for an additional adder wshoud the customer want to vrarify the design with a factory test.
That stuff was fun to sell.