Elect117
- California
- Engineer E.E. P.E.
I will break down for you my thoughts on it.
The short answer is yes. There is no code requirement that says you can not overload a transformer. Instead, you must not overload the conductor. So increasing the conductor can make you code compliant.
There are some design considerations to make as an engineer though.
1) Is this a facility that runs 24/7 at full load or is there down time over night? Most transformers that have time to cool overnight can be effectively overloaded with minimal or no loss of life expectancy. That is based on the temperature rise and insulating oil of the transformer and cooling method.
2) What will be the load based on 220.87? Take a years worth of metering info (even if it isn't a perfect match for the code) and calculate what you believe the demand will be. Be conservative a little and reach out to others if you are unsure.
3) Cost. Are you going to double the price of the project by suggesting increasing the size of the transformer? If they are prepared to upsize the transformer, it can be worth it if they see more expansions in the future. The cost today for the transformer and labor will be less than the cost 5 years from now.
I believe your transformer will be just fine to fulfill the 3000A board. I would up size the secondary runs for the new loads or add additional runs.