So you are saying bring the 3 ungrounded conductors, the equipment ground and the neutral to a 3-pole safety switch that is service rated?
 
250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).(A) Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.

Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non?current-carrying metal parts of equipment.

Roger

I was looking all over in 250 part III for the content that is in that exception. Any idea why this is not in part III? Seems like it should belong in that part to me.
 