goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I'm trying to understand the difference in the CMP's thinking between 210.4(B) and 210.7 (2014 NEC). Under 210.4 if I run a MWBC to a 2-gang JB and install two separate receptacles, this section infers that I have to use a 2-pole CB to disconnect all un-grounded conductors. Yet under 210.7, if I run two separate 120V branch circuits to a 2-gang JB and install two separate receptacles I am not required to use 2-pole CB's unless I snap off the tabs on the receptacles and install opposing circuits on the same yoke.
If the thinking was to disconnect all un-grounded conductors for safety reasons in the case of 210.4(B) why wouldn't the same logic be applied to 210.7?
If the thinking was to disconnect all un-grounded conductors for safety reasons in the case of 210.4(B) why wouldn't the same logic be applied to 210.7?