Can I run a mwbc from fuse box for two 20 amp outlets ? ( by code )
By code you need a way to simultaneously disconnect both ungrounded conductors where they originate. A case could be made for using a double pole switch next to the fuse box to satisfy 210.4(B).
How does a two-pole switch satisfy the condition of disconnecting at the point where the branch circuit originates? Under Code, a MWBC circuit originates at the terminals of the branch-circuit OCPD(s) and the grounded conductor terminal bus.I don't even think it is a 'case' I think it is a for sure you can do that.
It blows my mind that some insist it has to be a breaker.![]()
Probably Billy Idol fans....It blows my mind that some insist it has to be a breaker.![]()
I live in the same world as everyone else whether you REAL-ize it or not.Yeah OK. :lol:
You are free to live in the world linguists I will live in the world of electricians and commonsense.
You really believe the CMPs intention was to prevent the use of MWBCs with fuses? I find that notion absurd.
We see eye to eye on this point.I made my position clear and short of a CMP statement saying otherwise that is where I stand.
Happy Thanksgiving.![]()
He can run a MWBC from a fuse box...I see the real substance of the question now: op literally meant a fuse box......
...if the fuse box is a 2- or 3-pole fused disconnect.
I believe Code considers a fused disconnect as an integral unit consisting of a switch and fuse-type OCPDs. Under relevant sections, each is considered separately. A breaker is considered without differentiation for the very reason you stated.Is the fused disconnect as a whole considered to be OCPD or just to contain the fuses which are the actual OCPD?
With a breaker the OCPD contacts and the disconnect contacts are one and the same. :angel:
I just realized the other major difference between a fused disconnect and a disconnect after a fuse box:I believe Code considers a fused disconnect as an integral unit consisting of a switch and fuse-type OCPDs. Under relevant sections, each is considered separately. A breaker is considered without differentiation for the very reason you stated.
I see nothing in the code that would prohibit fuses from serving a MWBC. But I do not know, from a practical installation point of view, how to satisfy the rule about simultaneous disconnection. Let me echo Smart $'s question from post 5. Can anyone speak to that?