MWBC?

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Red insulated conductor to 15 amp breaker in left panel travels back into the right panel then wire-nut connects to a white insulated conductor that continues into another Type-NM cable (black insulated conductor is connected to a breaker in the right panel). Is this sort of a MWBC? Am I missing something?
 

Attachments

  • DSCF5885.jpg
    DSCF5885.jpg
    151.1 KB · Views: 0
Is there a proper neutral in the NM cable that lands on the neutral bar?

If not, I'd say it's a very jerry-rigged 2-pole circuit.
 
As either 2 pole circuit or an MWBC it violates the rule that all ungrounded circuit conductors must originate in the same panel.

Sent from my XT1585 using Tapatalk
 
It also violates the rule that says that a circuit breaker must open all ungrounded conductors simultaneously, again whether this is intended as a 2-pole circuit or a MWBC.

But I am curious. Are you saying that the red wire from the left is connected to a white wire on the right, so that the circuit leaving the right side panel has a white conductor that is energized? I would call that another violation, and a particularly dangerous one at that.
 
It also violates the rule that says that a circuit breaker must open all ungrounded conductors simultaneously, again whether this is intended as a 2-pole circuit or a MWBC.

But I am curious. Are you saying that the red wire from the left is connected to a white wire on the right, so that the circuit leaving the right side panel has a white conductor that is energized? I would call that another violation, and a particularly dangerous one at that.

Yes... white wire leave box at the top in an other Type-NM cable.
 
It could be a MWBC that the grounding conductor is being used as a Neutral, it could be a 240V circuit feeding a 240 machinery or heater with an EGC. At either case it does not sound a properly done circuit.

Disconnect both circuits and see what happens.
 
Last edited:
Red insulated conductor to 15 amp breaker in left panel travels back into the right panel then wire-nut connects to a white insulated conductor that continues into another Type-NM cable (black insulated conductor is connected to a breaker in the right panel). Is this sort of a MWBC? Am I missing something?
Careful reading of what was said in OP seems to describe a 2 wire NM cable (with ground?) with black conductor landing in a breaker in one panel and the white spliced onto a red conductor that lands on a breaker in the other panel. Seems that is likely a straight 240 volt circuit - but as is has a problem with handle ties/common trip requirements.
 