Yes, I have a copy of the 1899 code and the 1896 minutes, but want the real thing if you know what I mean...
Buried or driven electrodes shall, if practicable, have a resistance to ground not to exceed 25 ohms. If the resistance is not as low as 25 ohms, two or more electrodes connected in parallel shall be used.
Continuous underground water or gas pipe systems in general have a resistance to ground of less then 3 ohms. Metal frames of buildings and local metallic underground piping systems, metal well casings, and the like, have, in general, a resistance substantially below 25 ohms.
It is recommended that in locations where it is necessary to use buried or driven electrodes for grounding interior wiring systems, additional grounds, such as a connection to a system ground conductor, be placed on the distribution circuit. See 2533.
It is also recommended that single electrode grounds when installed, and periodically afterwards, be tested for resistance, particularly if there are no other grounds on the secondary distribution system.
It is also recommended that single electrode ground when installed, and periodically afterwards, be tested for resistance.
instead ofMade electrodes shall
buried or driven electrodes shall
A single electrode consisting of a rod, pipe, or plate which does not have a resistance to ground of 25 ohms or less be augmented by one additional electrode of a type specified in section 250-83 Made Electrodes.
When protective grounding is required, the suggestions given on the following pages 56 to 62 are in accordance with the recommendations of the Committee on Grounding of the National Fire Protection Association which were adopted October 17, 1917....
...The combined resistance of the ground wires, and connections of any grounded circuit, equipment, or lightning arrestor should not exceed 3 ohms for water pipe connections, nor 25 ohms for artificial grounds where these are used. Where because of dry or other high resistance soils it is impracticable to obtain ground resistance as low as 25 ohms, two such grounds 6 feet apart, if practicable, should be installed, and no requirement will be made as to resistance.