And this is the point of the code making panel concerning the rebar.
Unless the metal water pipe, ground rod, rebar (through contact with concrete) is in contact with earth then it is nothing more than a connection point and not the electrode.
In my opinion the five feet of metal water pipe on the inside or the two feet of a 10 foot rod sticking out of the ground and including the rebar that is turned up out to the footing is nothing more that what is described in 250.64(F)(3) and is not the electrode itself. The electrode must be in contact with earth no matter how useless it might be.
So if the rebar sticking beyound the cement is not an electrode (and IMO it is not) what is it?
Is it a GEC or is it a bonding jumper?
And where does the NEC give permission to use steel for either of those uses?