mivey
Senior Member
IMO, Crossman gary's follow-up post:Mike Whitt makes sense...
makes more sense.You say the two feet above ground
.
.
.
Read the book.
IMO, Crossman gary's follow-up post:Mike Whitt makes sense...
makes more sense.You say the two feet above ground
.
.
.
Read the book.
So.... CMP5.... please solve this issue by establishing that the rebar stub-up is part of the electrode, just as is done for building steel.
Sure, the text literally states that we can't connect outside of five feet. There is no literal permission to connect between zero and five feet.Care to explain what you differ with?
Knock yourself out, I've had this argument before and it didn't really change anyone's mind, that I can recall. :smile:Crossman said:I'll yield to George at the moment. If he doesn't want to attack it, I may myself.
You say the two feet above ground is not part of the electrode.
It is okay to disagree with me
I say you are misinterpreting what the code says about it.
Yes I do see that ?through which? part and I also see the part that says ?a direct connection to earth is established.? The two feet above earth is in no way in direct contact with earth. To say that the two feet above ground is the ?through which? would not the grounding electrode conductor also be the ?through which? also thereby making it an electrode.Notice the term "though which" in the definition. This does not say that "only the portion in contact with earth" can be an electrode. To make that determination, you must go to 250.52 and look at each electrode type individually.
For example, the entire metal frame of the building which meets the criteria in 250.52(A)(2) is an electrode. Yep, even the part on the 2nd floor. The building steel on the 2nd floor is part of the electrode as described in the section.
and we know this simply because the book says so. I haven?t heard any argument about the steel of a building.
That the building frame parts which are not in contact with the earth are still considered by the NEC as the electrode, yes, on the 2nd floor, just look at 250.52(A)(2)(3). None of the building frame is even touching earth, yet it is considered as an electrode.
Notice On the entire length of the rod being the electrode rather than just the portion below ground:
Again using this logic the entire length of wire supplying the electrode is part of the conducting path therefore you are saying that we don?t have a GEC as it is electrode also.
First, the definition - the entire rod is a conductive object THROUGH WHICH a direct connection to earth is made. The part of the rod above ground and the interior of the rod is the "through which" part. The very outside layer of atoms of the rod is the part that establishes the direct connection to earth.
Nowhere does the NEC infer anything. It is mostly cut and dry. On the part concerning grounding electrodes each section that address them clearly states that part that is in direct contact or underground is electrode and any part that isn?t is not part of the electrode. (remember we are addressing three of the electrodes, metal water pipe, rebar and driven electrodes)Notice Second, 250.52(A)(5) - doesn't say that only the part that is contacting earth is the electrode. It infers that the entire pipe or rod is the electrode.
I don?t think that anything is inferred I think it makes a clear statement. The rod is required to have 8 feet in contact with mother earth and it is this eight feet that constitutes the electrode. Anything above mother earth is just a rod sticking out of the ground for a wire to be attached to just like the bus bar allowed in 250.64.Notice Third, 250.53(G) - "The electrode shall be installed such that at least 8 feet is in contact with the soil." This infers/establishes that electrodes longer than 8 feet exist, but if you have a longer rod, for example, 10 feet, then you only have to drive it 8 feet.
Notice and read the last sentence of 250.53(G) - "The upper end of the electrode shall be flush with or below ground level unless the aboveground end and the GEC conductor attachment are protected against physical damage.
Not unless you are reading something different that what I am reading. Did you not say that the rod was required to be eight foot long? If eight feet is in the ground then the requirement for the electrode is satisfied and anything sticking out of the ground is nothing more than rod.
That last one positively says that if part of the rod is aboveground, it is still an electrode.
The sections definitely refer to the entire length of the rod being an electrode, not just the underground part.
I welcome any and all comments. I have the code section right here in front of me so I am prepared.Notice On the the waterpipe and the portion just inside the building... I'll yield to George at the moment. If he doesn't want to attack it, I may myself.
I could not agree more with this statement. I also know from experience that once someone steps out of the box it is easy to see that the walls they have been looking at for so long have another and completely different view.Notice Point is, you can't just use "sense" to determine what the code "says". You actually have to read the various sections and put in the effort to figure out what it literally says. Just because some of us "prefer" it to say something, or just because "it makes sense like that," or just because "I have always done it like that," is not good enough.
There are several people on this site that will attest that on average I will spend more time in the NEC in one day than most will in a year. I see and talk with those responsible for writing the NEC more often than some in here see their families.Notice Read the book.
Sure, the text literally states that we can't connect outside of five feet. There is no literal permission to connect between zero and five feet.
Prior to the five foot mandate introduced somewhere around 1986, the water pipe electrode was connected to outside of soil (outside of the area described in the definition of the electrode), and no one thought anything of it. Now, people point to the restriction as proof that we can. What proof did installers have in 1980?
That same proof then is what installers have now for the CEE.
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe. A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductors.
(End of sentence concerning the electrode)
(beginning of new sentence addressing part of the electrode SYSTEM which would include the conductor as this sentence points out)
Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system.
It sounds like a conductor to me.If so is the five feet of metal water pipe that is connected to the nonmetallic water pipe between it and the well now become an electrode.
It did call it a conductor. I was thinking it was more like part of the connection.It sounds like a conductor to me.
In that edition, was it required to run GECs unbroken to the GEs?jwelectric said:In the 1993 code cycle verbiage of the five feet of interior water pipe was introduced and in this code cycle these five feet was referred to as a conductor.
"Can you connect to a Ufer by stubbing up a piece of rebar out of the foundation and connecting your Grounding Electrode Conductor to it?"
Thanks for the correction about the dates, Mike. I'm at a disadvantage, I don't have any old code books.
I was just going off of memory, as far as what I had been told (in a previous thread on this from Pierre) about when the five-foot rule came into play, I remembered '83 when it should have been '93.
In that edition, was it required to run GECs unbroken to the GEs?
For example, in the 2008 edition we are required to make the GEC continuous (250.64(C)) from the service to the grounding busbar, or from the service to the grounding electrodes (250.64(F)). Was it the same in 1993?
(C) Continuous. Grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint except as permitted in (1) and (2):
What was it someone else had to say earlier in this thread?(1) Splicing shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.
(2) Sections of busbars shall be permitted to be connected together to form a grounding electrode conductor.
The whole of 250.64 is addressing the installation of the Grounding Electrode Conductor. I don?t see anything that tells me how to hit the grounding electrode. For this information I need to read just a little more of the NEC down in 250.68.Point is, you can't just use "sense" to determine what the code "says". You actually have to read the various sections and put in the effort to figure out what it literally says. Just because some of us "prefer" it to say something, or just because "it makes sense like that," or just because "I have always done it like that," is not good enough.
The reason I ask is because if the same basic rules were in place then, then we would not have been able to use that five feet anyway.
I can?t find any requirement to land directly to the electrode. I see many different allowances to land anywhere on the grounding electrode system even the extra two feet of a 10 foot ground rod. This allowance is given along with the allowance to use aluminum grounding electrode conductors as long as it is at least 18 inches from contact with earth. Eight feet in direct contact with earth is the electrode and the two feet above earth is what ensures an uninterrupted path to that electrode as required by 250.68 which mandates the connection of grounding electrode conductors and bonding jumpers that connect the electrodes together.As it stands, if one were to adopt the philosophy that we can only connect directly to the business portion of a grounding electrode, the five foot restriction means nothing, because we can't connect there anyway without specific permission. In for a penny, in for a pound.
And then 250.64(F) states that it's supposed to start in the service equipment, and end in either a grounding electrode busbar or at a grounding electrode, like I said.There is no requiremenr now or then for the GEC to be continuous from the grounded conductor to the electrode.For example, in the 2008 edition we are required to make the GEC continuous (250.64(C)) from the service to the grounding busbar, or from the service to the grounding electrodes (250.64(F)). Was it the same in 1993?
250.64(C) only requires the GEC to be continuous from one end to the other.
Just so you don't miss it again, I'm repeating it: 250.64(F).jwelectric said:It has no requirement at all as to where the two ends are to land.
No, it's not required to be accessible if the connection is buried. It's a buried electrode.jwelectric said:... 250.68.
Here we are told that the connection to the grounding electrode is required to be accessible. Exception 1 relieves this requirement for CEE, driven or buried electrodes. The metal water pipe is not mentioned in this exception therefore the connection to the metal water electrode is still required to be accessible.
Read the words, Mike. It does not. It places a prohibition on farther than five feet, it does not permit us to use zero to five feet.jwelectric said:250.52(A)(1) allows the first five feet of interior metal water pipes to be included in the grounding electrode system.
It doesn't mention that five feet at all, Mike. It can be applied to the entire installation of the grounding electrode.jwelectric said:250.68(B) says that should these five feet are used...
I fail to find specific permission to connect to the extra 2' of a ground rod. If you believe this to be assumed, you're halfway to my way of thinking already.jwelectric said:I see many different allowances to land anywhere on the grounding electrode system even the extra two feet of a 10 foot ground rod.
A wire connected to another wire by using a means that fuses the pair of wires together to become one wire. Hmm...On a building that has more than one service disconnect I can install one grounding electrode conductor and install bonding jumpers to the grounded service neutrals again the grounding electrode conductor is not continuous from neutral to electrode, 250.64(D)(1).
Any point on the system comprised exclusively of grounding electrodes and grounding electrode conductors. I don't see "A conductor used to connect the system grounded conductor or the equipment to a grounding electrode or to a point on the grounding electrode system, or an indescriminately selected chunk of something connected in some proximate means to one of the two."On this same building each disconnect can have its own grounding electrode conductor installed from the neutral in the service disconnect to any point on the grounding electrode system and again it is not required to hit any electrode 250.64(D)(2).
There is no requiremenr now or then for the GEC to be continuous from the grounded conductor to the electrode.
Okay let?s look and see where it gives instruction on how to terminate this ground electrode conductor in 250.64.250.64(C) only requires the GEC to be continuous from one end to the other. It has no requirement at all as to where the two ends are to land.
And then 250.64(F) states that it's supposed to start in the service equipment, and end in either a grounding electrode busbar or at a grounding electrode, like I said.
Just so you don't miss it again, I'm repeating it: 250.64(F).
jwelectric said:250.52(A)(1) allows the first five feet of interior metal water pipes to be included in the grounding electrode system.
It also does not require anyone to use the first five feet as anything either but it does refer in that same sentence as this five feet being part of the grounding electrode system and does not just say grounding electrode. Wonder why they found it necessary to use the word system instead of calling a grounding electrode?Read the words, Mike. It does not. It places a prohibition on farther than five feet, it does not permit us to use zero to five feet.jwelectric said:
Yes you are right is doesn?t say anything about the five feet but it does address the path that current would travel from the GEC through the five feet of pipe to the electrode that is required to be in direct contact with earth or in other words that part of the metal water pipe that is underground not swinging from a 2 by.It doesn't mention that five feet at all, Mike. It can be applied to the entire installation of the grounding electrode.jwelectric said:250.68(B) says that should these five feet are used...