Dean83169
Senior Member
I have worked on many large commercial and institutional projects. Most do not have emergency generators but my proposal would be directed to the portion of the code which relates to "if you have one circuit, the emergency lighting load must be tied to that circuit or if you have more then three you may pick one of the lines to tie to" I do not have the exact quote or article number.
My suggestion to change this is to monitor all legs within that room as so if ANY of the circuits trips then the emergency lighting would have to turn on.
I only say this due to the fact that you either need to have all the lights on or at least that circuit you tied to on in order to have emergency lighting. In the day of saving energy and the engineers installing to many lights, most cases you only use half the amount which could possibly result in no emergency lighting. I think it should change to have to monitor all phases of lighting in such rooms with multiple circuits. Any comments?
My suggestion to change this is to monitor all legs within that room as so if ANY of the circuits trips then the emergency lighting would have to turn on.
I only say this due to the fact that you either need to have all the lights on or at least that circuit you tied to on in order to have emergency lighting. In the day of saving energy and the engineers installing to many lights, most cases you only use half the amount which could possibly result in no emergency lighting. I think it should change to have to monitor all phases of lighting in such rooms with multiple circuits. Any comments?