Take a pic of the nameplate. It will tell all.
The internal fuse is not serviceable. There are two if I remember right, a primary and a back-up current limiting fuse for hard faults. The back-up fuses limits the short circuit energy in the can if I'm correct reducing the odds of the lid blowing off or oil going everywhere.
CSP units usually have a lever near the LV bushings.
I don't think that one has a lever, if it does it is probably a little further around the right side in that image. Lever will have a loop so it can be operated with a hook-stick.I see no lever on the side with the LV bushings, just a bonding strap...
After you mentioned the nameplate, I realized I was taking a picture of an ordering label. I assume the nameplate is that black label on the bottom bracket for the pole mount - it's partly visible in my post #23. That's a tomorrow problem for sure, getting that picture. Sure would have been easier to snap that picture while it was on the ground
Thanks kindly again for the info.
I see no lever on the side with the LV bushings, just a bonding strap...
After you mentioned the nameplate, I realized I was taking a picture of an ordering label. I assume the nameplate is that black label on the bottom bracket for the pole mount - it's partly visible in my post #23. That's a tomorrow problem for sure, getting that picture. Sure would have been easier to snap that picture while it was on the ground
Thanks kindly again for the info.
Yes, the black label will tell all! In so far not a CSP as I can tell. I have a soft spot for that red overload light.
No. We do it daily.
Quick question... I understand the 2 schematics at the bottom, the right side is more standard for 120/240V but you could put both halves of the secondary in parallel to get 2x the current for 120V only (as shown on the left). But how do you rewire it? Do you have to take the top off? Are the connections inside buried under oil? And would this 120V re-wire be fairly unusual to do in the field.
No. We do it daily.
ask any lineman about “alley cat, bad dog”
Yes, the internal secondary conductors must be reconfigured by hand.But you still take the cover off, right?
BTW, now do you see why they consider the incoming service "unfused"? 10 amp fuse with time current curve that starts at about 20 amps. You would have to load the bank well over 150kva to blow something quickly.
No. We do it daily.
ask any lineman about “alley cat, bad dog”
Yes, I do. Yikes - if I am reading those curves correctly, you'd need to draw ~45A to open that 10 amp fuse in 1 sec. That's almost 14x the rating of the transformer. Clearly the fuse is for serious problems and they are happy to let the pot ride out small overloads like you pointed out earlier. And when mine let go on Friday, that kind of energy "input" likely let some serious heat build up. Can't fault the oil for wanting to find its way out of Dodge.
And yes, I now understand how the 120 only is for building a 3 phase bank, I assume it would have to built as Wye-Wye, since this transformer has one side of the primary grounded to the can? Whereas a Delta primary would need pots with 2 floating bushings?