So how much THD is required for a load to be considered "nonlinear" for the purposes 2023 NEC 310.15(E)(3) anyway?
If the load's current waveform has say 10% THD, and if that harmonic distortion consists solely of 3k-order harmonics (k any natural number), then the neutral current on a balanced 3-phase set of 3 such loads would be 30% of the line current. The heating would 3.09 times the heating from one line conductor, rather than 3 times the heating from one line conductor if the neutral currents perfectly cancelled. Seems like a small enough change that an 80% ampacity factor (with according 36% reduction in heating) should not be triggered.
Cheers, Wayne
If the load's current waveform has say 10% THD, and if that harmonic distortion consists solely of 3k-order harmonics (k any natural number), then the neutral current on a balanced 3-phase set of 3 such loads would be 30% of the line current. The heating would 3.09 times the heating from one line conductor, rather than 3 times the heating from one line conductor if the neutral currents perfectly cancelled. Seems like a small enough change that an 80% ampacity factor (with according 36% reduction in heating) should not be triggered.