Sounds like a title for a UFO movie? My brother called me last night and apparently this has been going since February of this year (2006). Since I was an electrician and now HVAC person I seem to get these calls from friends and relatives alike.
From January to February his Kw/H?s usage doubled. He lives in a old house he has remodeled and is now semi-retired. Just he and his wife and one son live at home. They have a electric dryer, stove and water heater, all appliances are newer. He also has an underground feeder (3 years old) taking 230 volts out to his detached garage.
He has had two electricians check things out, and one replaced the service mast conduit and wires to his newer service panel. The power company also replaced his meter. Since I only live about 2 hours from his place, I?m sure I will be up to check things for him.
The extra 1000 Kw/H?s a month or so works out to about 5 or 6 amps on 230 volts or 11 ? 12 amps on 120 volts 24/7. My suggestion on the phone last night was three things; he start checking circuits with a clamp on ampmeter at random times, his electric water heater might have an element that has shorted out and taking current to ground inside the tank, or more than likely the underground to his garage has insulation breakdown and he is losing current to earth ground. I?m open to any other ideas?
From January to February his Kw/H?s usage doubled. He lives in a old house he has remodeled and is now semi-retired. Just he and his wife and one son live at home. They have a electric dryer, stove and water heater, all appliances are newer. He also has an underground feeder (3 years old) taking 230 volts out to his detached garage.
He has had two electricians check things out, and one replaced the service mast conduit and wires to his newer service panel. The power company also replaced his meter. Since I only live about 2 hours from his place, I?m sure I will be up to check things for him.
The extra 1000 Kw/H?s a month or so works out to about 5 or 6 amps on 230 volts or 11 ? 12 amps on 120 volts 24/7. My suggestion on the phone last night was three things; he start checking circuits with a clamp on ampmeter at random times, his electric water heater might have an element that has shorted out and taking current to ground inside the tank, or more than likely the underground to his garage has insulation breakdown and he is losing current to earth ground. I?m open to any other ideas?