Power Loss
Power Loss
Well I'm headed up tomorrow (Sat. 6/29/06) to see what I can find. In the past week or so I've given him some homework and this is what he's found:
Now bear in mind we are talking kWH usage here per month has doubled. His meter was changed to a digital one, so he can easily read the usage per day, which is about 80. Also somewhere along the way he has purchased a clamp on amp meter. BTW he has checked by R&R and inspection the water heater elements. So in the course of amping things he discovered that on each of his two separate GEC, one to the "new" ground rod outside, the other "old" one connected to his really old copper/steel water system going to the street in lead pipe. Did I say really old? Anyway they both are reading some amperes. Which I understand is normal.
My suggestion to him was to clean up the old water pipe ground connection and land it in his service box right on, or as close as he could get to the new ground,(all done by a local electrician.) Now he has nearly 11 amps or so on these ground wire(s) when turning on some 120 volt only loads.
My question before I get up there, I would assume that 0 zero amps on the GECs would be ideal. But am I correct in thinking that the higher the amp draw, the more likely the PoCo neutral connection at the really old power pole connection, is not good. The town is so small they have to sub contract out the repairs on the power lines, which means they would need to spend money to actually have someone come out from 30 miles away to fix.
And now the really good question... what does all this have to do with increased kWh usage??
Power Loss
andycook said:I found an 1 1/4 EMT service entrance conduit that had been cut open (?)(POCO side of meter) and the #2 wires tapped. The tapped wires went into the ground and disappeared. Never could find where they went. I cut off the taps and taped them up.
The HO had lived there for 20 years, and never noticed (it was in a detached garage. I gave them a price to replace the service. They were low on funds, so they had a cousin from out of town come up and replace the service.
Truth is stranger then fiction!
Well I'm headed up tomorrow (Sat. 6/29/06) to see what I can find. In the past week or so I've given him some homework and this is what he's found:
Now bear in mind we are talking kWH usage here per month has doubled. His meter was changed to a digital one, so he can easily read the usage per day, which is about 80. Also somewhere along the way he has purchased a clamp on amp meter. BTW he has checked by R&R and inspection the water heater elements. So in the course of amping things he discovered that on each of his two separate GEC, one to the "new" ground rod outside, the other "old" one connected to his really old copper/steel water system going to the street in lead pipe. Did I say really old? Anyway they both are reading some amperes. Which I understand is normal.
My suggestion to him was to clean up the old water pipe ground connection and land it in his service box right on, or as close as he could get to the new ground,(all done by a local electrician.) Now he has nearly 11 amps or so on these ground wire(s) when turning on some 120 volt only loads.
My question before I get up there, I would assume that 0 zero amps on the GECs would be ideal. But am I correct in thinking that the higher the amp draw, the more likely the PoCo neutral connection at the really old power pole connection, is not good. The town is so small they have to sub contract out the repairs on the power lines, which means they would need to spend money to actually have someone come out from 30 miles away to fix.
And now the really good question... what does all this have to do with increased kWh usage??