The great and powerful Oz has spokenOriginally posted by html:
Hey oh great wizards of the 2002 NEC
Bob334.15(C) In Unfinished Basements. Where the cable is run at angles with joists in unfinished basements, it shall be permissible to secure cables not smaller than two 6 AWG or three 8 AWG conductors directly to the lower edges of the joists. Smaller cables shall be run either through bored holes in joists or on running boards.
How about I be Oz and you be Odd? LMAOOriginally posted by iwire:
[QB] Ryan you beat me I wanted to be the wizard.![]()
Other than that, I am at a loss, looks like I have to turn in my pointy hat.334.15 Exposed Work.
In exposed work, except as provided in 300.11(A), the cable shall be installed as specified in 334.15(A) through (C).
(A) To Follow Surface. The cable shall closely follow the surface of the building finish or of running boards.