Our area inspectors have always enforced using the outside holes on deep boxes with 2x4 studs
Our area inspectors have always enforced using the outside holes on deep boxes with 2x4 studs
It enters the box within 1 1/4" of the edge of the stud or joist.
It says "installed" parallel. That means where it is attached.
Not my job to protect from stupid. Yes the nails went through the wires.
View attachment 7255
So don't use the cable entry that is within 1-1/4 inch of the stud then. Or use a 1-1/4 inch or thicker block to move the box away from the stud.
If not your job to protect from stupid, did you make them replace the cables?
It's still a nailing surface.
Did the inspection not the install.
How about using those cable stackers?
Our area inspectors have always enforced using the outside holes on deep boxes with 2x4 studs
Don't think it's just the NM on the stud, he is saying the back of the plastic boxes that are closer than 1-1/4" need to be covered by a plate. This means use a 4sq. blank to cover the back of most plastic boxes.
Are we speaking of 300.4 because I read it as pertaining to the cable or raceway. So how is the box a cable or raceway? It is part of the system but it is not either a cable or a raceway.
acrwc10Don't think it's just the NM on the stud, he is saying the back of the plastic boxes that are closer than 1-1/4" need to be covered by a plate. This means use a 4sq. blank to cover the back of most plastic boxes.
The problem is the cable enters the box closer than 1.25" from the front edge of the stud.
The problem is the cable enters the box closer than 1.25" from the front edge of the stud.