Is this installation code compliant where the cable is less than 1.25" from the edge of the stud?
If I run the cable on the side of the stud a space of 1.25" must be maintained or protection is required. Would the same 1.25" apply to the conductor behind the nail plate? What does it mean that it is required "to cover the area of the wiring"?
If I run the cable on the side of the stud a space of 1.25" must be maintained or protection is required. Would the same 1.25" apply to the conductor behind the nail plate? What does it mean that it is required "to cover the area of the wiring"?
300.4(A) Cables and Raceways Through Wood Members.
(1) Bored Holes. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed through bored holes in joists, rafters, or wood members, holes shall be bored so that the edge of the hole is not less than 32 mm (1 1 ∕ 4 in.) from the nearest edge of the wood member. Where this distance cannot be maintained, the cable or raceway shall be protected from penetration by screws or nails by a steel plate(s) or bushing(s), at least 1.6 mm ( 1 ∕ 16 in.) thick, and of appropriate length and width installed to cover the area of the wiring.