name plates

Status
Not open for further replies.

Mzwakhe

New member
name plate information; i am looking for a document which explaines how to read name plates of tranformers and motors!:confused:
 

zog

Senior Member
Location
Charlotte, NC
OK, look at the pic attached, here is what that all means.

Top The manufacturer (optional) and the name of the equipment, in simplified terms

KVA Kilovolt-ampere ratings are based on the type of cooling class and the desired temperature rise.

Class OA: Oil-Immersed, self-cooled

Cont. Rise 55/65 oC are two ratings at which the transformer can operate continuously. The higher the temperature allowed, the higher the rating. It should be noted that a high ambient temperature rise on hot days could shorten transformer life.

HV 24,900. The primary line-to-line nominal voltage

LV 480Y / 277. The secondary Wye connection voltage, line-to-line / line-to-neutral (single phase).

% IZ 5.7% impedance voltage at 75 oC

MFG DATE Manufacturing date

BIL Basic Impulse Level of windings.

HV/LV AL/AL. The conductors are aluminum.
CONDUCT

NOTES The note section in this transformer declares that PCB contamination is less than one (1) parts per million (PPM).

APPR. Weights are critically important when installing, moving, or
WEIGHTS un-tanking the transformer.

TAP This box shows the no-load tap changer positions A - E for the line (high voltage) input to the transformer. 24,940 is in the center (C).

MAX AMPS Based on 840KVA. Varies inversely with the voltage setting of the tap.

DIAGRAMS The diagrams show (1) connection scheme, (2) angular displacement, and (3) physical bushing arrangement as viewed from the top.

Hope this helps
 

mivey

Senior Member
You may also find these notes about power transformer notation useful:
Symbol -- Example -- Explanation
E -- 12470 -- Δ connection on E volt system
E/E1Y -- 7200/12470Y -- Δ connection on E volt system or Y connection on E1 volt system
E/E1GrdY -- 7200/12470GrdY -- Reduced insulation for Y connection on E1 volt system with transformer neutral effectively grounded or for Δ connection on E volt system.
E1GrdY/E -- 12470GrdY/7200 -- Reduced insulation at the neutral end. The neutral may be connected directly to the tank for connecting single phase or in Y on an E1 volt system with the neutral end of the winding effectively grounded.
E/2E -- 120/240 -- Winding for multiple, series, or 3-wire service
2E/E -- 240/120 -- Winding for 2E volts, 2-wire full kVA, or for 2E/E volts 3-wire service with 1/2 kVA available from mid-point to each outside terminal
"Ex2E -- 1st ex:240x480 2nd ex:2400/4160Yx4800/8320Y -- Winding for multiple or series operation only (not for 3-wire service)"
 

megloff11x

Senior Member
NEC 430 says what the nameplate should have. I think someone should make a copy and send it to EVERYONE who makes motors as I have yet to see a motor with all the information required actually provided on the nameplate.

We got in some foreign made widget with foreign motors, and rather than try and puzzle through their specs and figure out what would happen if we ran it through a transformer to get the right Voltage and possibly a VFD to get the right frequency, we just chucked it and made them buy a domestic motor of the same approximate HP as this was cheaper than trying to make the one that came with it run like it was supposed to.