Is the bubble required in a 'vault?' I'm assuming it's a protected room/pit/etc.The obvious ones
- Lack of OCPD on the added taps to the main distribution blocks in the cabinet
- SO cable exiting cabinet without proper cable gland for strain relief
- Missing bubble cover on the right GFCI
- Cables not secured or strain relieved to the VFD on the wall
- SO used in place of fixed wiring method
- SO not properly secured
- BX clamps used on SO
- Working space violations