OK a little background. I have a 30 KVA transformer, Primary is corner grounded delta 480v , secondary is 120/208 center grounded wye. Now the problem; without load my power is clean 120/208+ no problem, after putting standard 120 volt load on I have a loss of power on one hot leg (0 volts) and the neutral becomes the hot leg?? all connections and taps have been triple checked help. yes i typed this right without load x1-120 x2-120 x3-120 x0-0, with load x1-0 x2-120 x3-120 x0-120 or else an odd one like x1-98 x2-120 x3-120 x0-28 ANY help woul be great