OK a little background. I have a 30 KVA transformer, Primary is corner grounded delta 480v , secondary is 120/208 center grounded wye. Now the problem; without load my power is clean 120/208+ no problem, after putting standard 120 volt load on I have a loss of power on one hot leg (0 volts) and the neutral becomes the hot leg?? all connections and taps have been triple checked help. yes i typed this right without load x1-120 x2-120 x3-120 x0-0, with load x1-0 x2-120 x3-120 x0-120 or else an odd one like x1-98 x2-120 x3-120 x0-28 ANY help woul be great
 
Re: nasty three phase problem

Need more information. Are you saying that the leg you connect the load to goes to 0V and the others stay at 120? What is the reference point for your measurements? Is this true of all legs or just one? Also have you connected 208V loads?
 
Re: nasty three phase problem

Let me get long winded here. This is in a computer room at the industrial plant where I work. I was called in by the comp tech when he installed new UPS units, as they were fault coding "improper wired receptacle". Using a standard "quick check" hot/nuetral/ground tester, it showed reversed polarity on the grounded/hot wires. I checked all wires to the panel to see if colors/ polarity had been reversed and found nothing. So I checked the incoming wiring and found the neutral to be 120 volt (Isolated ground). I promptly shut the main breaker off and retested, all incoming wiring is now OK 120 volt on each leg. I shut off all branch circuit breakers and turned on the main - still OK. I turned on the receptacle breaker and switheroo the hot is now 0 volts and the nuetral is 120 volts.
 
Re: nasty three phase problem

oh, didn't answer your question totally. No 208 loads are in this panel, I have no idea why the original electrician installed a 120/208 three phase panel. 120 loads are lights in three offices, general receptacles in two offices and two designated circuits in the computer room.
 
Re: nasty three phase problem

Why are you corner grounding the delta primary,in trying to derive 208/120 "Y"-3phase secondary?
 
Re: nasty three phase problem

Existing transformer. Incoming power to plant is 480 volt corner grounded delta. The secondary is 120/208 wye (center ground for nuetral). I do not know if this has been a problem before, I am new to tne facility.
 
Re: nasty three phase problem

I am still trying to get a handle on this. Are you taking the voltage measurements at the panel at the load side of the breaker? When you say the neutral is 120V where is the reference point,i.e 120V to what? Is voltage at receptacles on the other two phases correct polarity?
 
Re: nasty three phase problem

All references are to earth ie. GEC to existing grounding conductor, and building steel, transformer is likewise bonded to the same. Ground into panel box is isolated, and as there is no "neutral" in primary lines, transformer is neutral producing.
 
Re: nasty three phase problem

The problem seems to be just on the one leg, and just with the receptacles in the computer room. I have not torn into the lghting circuit, and other receptacles do not seem to have the same problem (which may mean they are not on that phase, or that I just haven't had any problem with it)!
 
Re: nasty three phase problem

Sounds like you have the hot and neutral crossed somewhere between the breaker and receptacle. If there are more than one recep in a daisy chain, this could easily be the case.
 
Re: nasty three phase problem

mixedbag,
I have no idea why the original electrician installed a 120/208 three phase panel.
What other type of panel would be installed on a 3 phase system?
without load x1-120 x2-120 x3-120 x0-0, with load x1-0 x2-120 x3-120 x0-120 or else an odd one like x1-98 x2-120 x3-120 x0-28 ANY help woul be great
Does the equipment connected between X1 and X0 work? I expect that it does. It is my opinion, as dillon said earlier, that you are missing the connection between X0 and the grounding system.
Don
 
Re: nasty three phase problem

I am totally unworthy to add to this, but I'm going to anyway.

I had a similar event in a (don't laugh) apartment. No load, everything was fine. Whenever there was a load applied, I'd get hot-neutral reverse. The problem was a loose neutral in the service where the meter banks coupled to the disconnect.

Have you checked all of your connections? :)
 
Re: nasty three phase problem

after putting standard 120 volt load on I have a loss of power on one hot leg (0 volts) and the neutral becomes the hot leg??
Loss of power on one hot leg also sounds like an open somewhere in the transformer (maybe an open secondary winding). If the other posts don't help, you might try checking that.

Steve
 
Re: nasty three phase problem

I agree with dillon & don, it sounds like X0 wasn't bonded and your neutral is floating.
 
Re: nasty three phase problem

Thank you Dillon, and Don. I tore back into the system tody, and found the transformer was not bonded, after correcting this, the voltages are safely where the belong - Mixedbag
 