I have in the past sought approval from the AHJ in accordance with Article 700.12 and utilized natural gas generators without issue.
A colleague under similar circumstances has specified gas generators for Article 700 applications only to find that the gas pressure has proven to be problematic. i.e. at certain times of the day, it's fine. At other times, it's a problem. The problem is not that the unit won't run but that it won't start up in the requisite 10 seconds.
He claims he's seen this scenario multiple times and that specifying gas generators for Emergency applications is a bad idea - should never be done - etc.. This seems a bit extreme. I was wondering what the experience has been of this group of "know it alls "
A colleague under similar circumstances has specified gas generators for Article 700 applications only to find that the gas pressure has proven to be problematic. i.e. at certain times of the day, it's fine. At other times, it's a problem. The problem is not that the unit won't run but that it won't start up in the requisite 10 seconds.
He claims he's seen this scenario multiple times and that specifying gas generators for Emergency applications is a bad idea - should never be done - etc.. This seems a bit extreme. I was wondering what the experience has been of this group of "know it alls "