Internal diameter D and pressure drop H are not related that way.another way to look at it is equivalent lengths
assume 1000' pipe
900 of 2"
100 of 1"
it's not a 1" restriction or drop
it's a 1000' pipe of 900/1000 x 2" + 100/1000 x 1" = 1.9" pipe
For a gas piping systems with smooth walls and a pressure of 1.5 psi or less, 2015 International Fuel Gas Code Equation 4.1 says D is proportional to H-0.206, which means that H is proportional to D-4.85.
Assuming in your example that 1" and 2" are the internal diameters (for ease of calculation), then the equivalent diameter would be given by Dequiv-4.85 = 0.9 * 2-4.85 + 0.1 * 1-4.85, which implies Dequiv = 1.52".
Cheers, Wayne