LarryFine said:I am saying that the arc cleared itself quickly enough to not reach the trip curve of the breaker. Whether that fell within the design parameters of that breaker cannot be determined without examination.
To my field-educated eyes, the maginitude of the soot indicates that there was a small explosion, and not a (relatively) long-duration fire. I believe the arc extinguished as fast as it started, and no tripped breaker.
As for starting a fire, In my opinion, the conduit system performed its function, which is as much to protect the building and people from damage by the wiring as it is to protect the wiring itself from damage.
This building is littered (and I use the term littered as a real description) with this type of Square D panel. I don't know the designation, but they are large brown 15A bolt in breakers (I've tenatively dated them to the early 1950's). I've seen them fail to trip under even severe faults.
6-7 months ago, I had one fail right outside my office. I had a power event in the office, everything failed over to backup and I heard the transformer on the floor below thump when it reenergized. Recognizing that it was something bad enough to draw down the supply voltage to the transformer (fed from a 600A 240D entrance), I immediately went to investigate and found the stairwell full of smoke.
On investigation, I found that a circuit on one of these panels had faulted, the breaker had failed to trip, and the resultant overload had dragged the voltage down for an instant until the fault cleared itself by burning the terminals off the breaker. The arc destroyed the bus bar and burned a hole right thru the insulator sheet to the frame of the panel.
These things make me REALLY nervous, so it's my mission at the moment to make them gone :smile: .
I agree re the conduit, obviously it did what it was supposed to.
Vern