klm0824
- Baton Rouge, LA
An existing 480V system has 500kcmil THWN/THHN cable fed from an existing 400A circuit breaker with 75 degree terminations. Routing is overhead RGS conduit. At first glance, the 400A breaker does not protect the 500kcmil.
Using table 310.16, 75 degree column, at 40 degree ambient, the ampacity is 334 amps - which would require a 350 amp breaker. The way I understand article 110.14(C) is that I can use the 90 degree ampacity (430A) and its derating factor (.91) to calculate the cable ampacity (391A), compare this ampacity to the 75 degree ampacity (380A) and use the smaller of the two (380A). This would allow the 400A circuit breaker to protect the 500kcmil.
Problem is that I don't understand how you can put 380 amps (vs 334 amps) on the 75 degree wire with a 40 degree ambient and not exceed 75 degrees. In this case, the insulation is the same for both ratings, and the copper has the same losses. And, what exactly does putting more that 75 degrees on a 75 degree termination do to the termination?