But isn't that not worst case scenario? Where does it say you're allowed to use .01 seconds if the chart just cuts off at that time?You would typically use .01 sec, unless you can get specific information from the manufacturer.
You cannot extrapolate any performance beyond what is shown on the TCC.
It is the worst case scenario. But you don't know what you don't know. The TCC stops at 0.01 seconds, so it will clear at 0.01 or faster.But isn't that not worst case scenario? Where does it say you're allowed to use .01 seconds if the chart just cuts off at that time?
Got it, so in my example my label on the service disconnect will be:It is the worst case scenario. But you don't know what you don't know. The TCC stops at 0.01 seconds, so it will clear at 0.01 or faster.
Seems correct to me based on the 2020 NEC. The language is different in the 2023 NEC.Got it, so in my example my label on the service disconnect will be:
Nominal system voltage: 208V 3-phase
Available fault current: 125,000 amps
Clearing time: 0.01 sec
Date: 3/14/2025
Is this correct?
NYC came out with a 2025 electrical code based on 2020 version so I'm trying to get familiar with the 2020 version. NYC is now requiring arc flash studies since they jumped to the 2020 version of the code.Seems correct to me based on the 2020 NEC. The language is different in the 2023 NEC
I have another question.Seems correct to me based on the 2020 NEC. The language is different in the 2023 NEC.
This is from the 2020 Handbook
View attachment 2576152
I always placed my label near the customer's nameplate, if they had one, otherwise it went near the manufacturer's nameplate. It was not uncommon to have multiple copies of the same lable on one long piece of equipment.Where do I place the label? Do I place it on sections 1 and 2 since it's the service side? Or do I just place it only on section 2?