We bought theses labels from Consolidated electrical distributor(CED) "these labels were not printed on our label maker" these were legitimate labels. It took them 4 days to give me the spec sheet I'm guessing because they were never ask for it before, just like I was never ask by a Inspecter if these stickers are gonna last the lifetime of the PV array, we emailed the spec sheet to the head Inspecter, he passed us ,but on further installs he wants the foil type labels, on top of that he wants a plaque for the (rapid shut down) no stickers
Since I have no information on how you have achieved the rapid shutdown and the environment you are at I figured a code section or 2 might produce light on he's making code up issue or an interpretation.
What is sufficiently durable? Inside maybe paper labels - outside plastic plaques? or ANSI Z535.4 Safety Labels Description -- Adhesive Backed Polyester Labels have been designed to comply with ANSI Z535.4 2002 & 2007 Product Safety Label Standards. Labels are screen printed with UV resistant inks and over laminated with Clear Polyester
to ensure a high degree of chemical, abrasion and heat resistance. If your labeling fits this criteria I'd say you have an argument.
Identified? Generally is already labeled as part of the equipment so no extra identification is necessary
but 690.56 has clear language having the option of a
permanent plaque or directory as requirement but still leaves room to have a minimum of ANSI Z535.4
110.21 Marking
( B) Field-Applied Hazard Markings. Where caution, warning, or danger signs or labels are required by this
Code, the labels shall meet the following requirements:
(3) The label shall be of
sufficient durability to withstand the environment involved.
690.12 Rapid Shutdown of PV Systems on Buildings
PV system circuits installed on or in buildings shall include a rapid shutdown function that controls specific conductors in accordance with 690.12(1) through (5) as follows.
(5) Equipment that performs the rapid shutdown shall be listed
and identified.
690.56 Identification of Power Sources
(C) Facilities with Rapid Shutdown. Buildings or structures with both utility service and a PV system, complying with 690.12,
shall have a permanent plaque or directory including the following wording:
PHOTOVOLTAIC SYSTEM EQUIPPED WITH RAPID SHUTDOWN
The plaque or directory shall be reflective, with all letters capitalized and having a minimum height of 9.5 mm (3⁄8 in.), in white on red background.