NEC 110.24

Status
Not open for further replies.

mannyb

Senior Member
Location
Florida
Occupation
Electrician
we are bidding 10k square building with 3000a service. The drawings provide no fault calculations for 110.24 or any calculations for 110.16 a or b. If the engineer hasnt provided neither and the EC is to provide as part of the bid what do you guys recommend to use like a software or do you recommend subbing that portion of work?
 
we are bidding 10k square building with 3000a service. The drawings provide no fault calculations for 110.24 or any calculations for 110.16 a or b. If the engineer hasnt provided neither and the EC is to provide as part of the bid what do you guys recommend to use like a software or do you recommend subbing that portion of work?

Either SKM or ETAP. If i am not mistaken, you are only required to mark the service equipment. This can be done with a single calculation for available short circuit current using the exact utility transformer impedance, secondary cable size/length, system voltage, etc. Utilize the infinite bus method unless you can get actual utility amps for the provider.
 