110.25(A) covers "working space" in front of equipment likely to "likely to require examination, adjustment, servicing, or maintenance while energized "
and generally requires 6 1/2 feet of vertical working space in front.
In my area of older buildings the electrical panels are often in hatches built into the exterior wall.
But we have to the rescue, at least for the smaller buildings:
That reads "units" not "dwellings". How would you interpret this clause for the set of common meters to a dwelling, not specific to a given unit in that dwelling? Does "dwelling unit" refer to a unit in the dwelling, or to entire buildings?
If a breaker exists in front of the equipment (e.g. it can be turned off but might not actually be turned off) is it still "likely to require examination, adjustment, servicing, or maintenance while energized "?
and generally requires 6 1/2 feet of vertical working space in front.
In my area of older buildings the electrical panels are often in hatches built into the exterior wall.
But we have to the rescue, at least for the smaller buildings:
Exception No. 2: In existing dwelling units, service equipment or enclosed panelboards that do not exceed 200 amperes shall be permitted in spaces where the height of the working space is less than 2.0 m (61⁄2 ft).
That reads "units" not "dwellings". How would you interpret this clause for the set of common meters to a dwelling, not specific to a given unit in that dwelling? Does "dwelling unit" refer to a unit in the dwelling, or to entire buildings?
If a breaker exists in front of the equipment (e.g. it can be turned off but might not actually be turned off) is it still "likely to require examination, adjustment, servicing, or maintenance while energized "?