NEC 110.26(C)(2) clearance requirement

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
See attached picture, to meet NEC 110.26(C)(2) and exhibit 110.20, should a new door be added to North East the room
enough?
 

Attachments

  • elec room.PNG
    elec room.PNG
    97.2 KB · Views: 26

gh0st

Member
Location
California
Occupation
Designer
If you have double the clearances maintained a second door is not required. Even so, adding the door would probably be recommended. Hate to be trapped back there during an arcing event.
 
Status
Not open for further replies.
Top