A anbm Senior Member Location TX Occupation Designer Mar 17, 2022 #1 See attached picture, to meet NEC 110.26(C)(2) and exhibit 110.20, should a new door be added to North East the room enough? Attachments elec room.PNG 97.2 KB · Views: 26
See attached picture, to meet NEC 110.26(C)(2) and exhibit 110.20, should a new door be added to North East the room enough?
G gh0st Member Location California Occupation Designer Mar 17, 2022 #2 If you have double the clearances maintained a second door is not required. Even so, adding the door would probably be recommended. Hate to be trapped back there during an arcing event.
If you have double the clearances maintained a second door is not required. Even so, adding the door would probably be recommended. Hate to be trapped back there during an arcing event.